I have a model 55020 (10 kw) generator with a wireless monitor. The monitor is now displaying an alarm message "Warning Sevice Date". It has been a year since the generator was installed. All maintenance has been performed by me as required. The generator display shows no alarm. How do I clear the alarm? The monitor has a slide switch on its left side. Does anyone know its function?
Quote
Skip Douglas SkipD
hksacks;8781 wrote:
I have a model 55020 (10 kw) generator with a wireless monitor. The monitor is now displaying an alarm message "Warning Sevice Date". It has been a year since the generator was installed. All maintenance has been performed by me as required. The generator display shows no alarm. How do I clear the alarm? The monitor has a slide switch on its left side. Does anyone know its function?
I don't have that generation of generator and thus don't have hands-on experience. I do believe, though, that the alert is time-based. There's a clear function in the menu that your book should help you access.
Skip Douglas
Quote
hksacks
Unfortunately, the only clear function is for the history. I've done that but the alarm doesn't go away.
Quote
Skip Douglas SkipD
Others with more knowledge of that generation of controller should be along to help.....
Skip Douglas
Quote
hksacks
SkipD;8788 wrote:
Others with more knowledge of that generation of controller should be along to help.....

FYI - I found the answer. There is a "Reset Maintenance" option on the generator display panel under the edit menu. That does the trick. The switch is an on/off!