JonC
New installation, model#G0070421. Generator starts, runs but will not transfer. Manual transfer works and unit will retransfer when power is restored. Looked at all obvious stuff like connections etc. and checked fuses. Anyone?
Quote
BrentB
Wire 23 is not going to ground inside the control board. Wire 23 is broken between the control board and the transfer switch. Turn on the breaker on the genset. Transfer can't occur without 240 VAC going into the stand-by coil. Make sure the coil wires are both plugged in to the base of the coil. make sure the lower limit switch has both wires plugged in, and the limit switch isn't stuck.
Quote
JonC
Thanks, I won't be able to return until Monday. I did a visual check of all connections and everything looked ok. I'll check the switch then.
Quote
JonC
I found my problem. I always use black and red for DC common and 12v +. I used red in the xfer switch and red with black trace in the generator. How did I do JoeL?
Quote
JoeL
LOL, you did good Jon
Quote