Unit manufacture date June 2015, 10/11kW - natural gas
Installed dec 2015 by certified gen guys. 
Model # 0067201 
Serial # 9740180 

its oil, but not enough to leave the black area, its just under the hose, and not very much.
but its coming  from somewhere .
possibly that hose clamp is what im thinking .
input is appreciated as usual
tia
Quote
Geoff Z
Those clamps are notorious for leaking. Our techs usually recommend swapping out suspect clamps with old school screw type radiator clamps. 
Quote
78buckshot
If you can pin-point it to the hoses and clamps then do what Geoff said, if that doesn't take care of it then I would suspect the crankcase breather is seeping and blowing oil on the engine base.
Quote
CTFSHJOHN
THANKS
yeah they did the breather gasket and main seal in jan 2018, low hours since then.
i hope its not that damn gasket again , the leak was different then i saw oil from elsewhere at that time.
Geoff Z wrote:
Those clamps are notorious for leaking. Our techs usually recommend swapping out suspect clamps with old school screw type radiator clamps. 

yeah i was looking at those clamps, is there a tension control on them at all?
Quote
78buckshot
I squeeze them with a pair of off-set diagonal wire cutters but prefer to replace the clamps, should be good-to-go on the breather.
Quote
JayH
Probably the clamp, it looks like a PEX clamp. I'd replace it with a worm type. Generac saved a few cents by using that clamp. Clean the area and dust the hose and fitting with flour, then check in a day or two to spot the source of the leak for sure.
Quote
CTFSHJOHN
going to go buy fuel injection clamps, what size am i looking for ?
thanks
Quote
78buckshot
The hose is metric, 9mm, that's the inside diameter, we call it 3/8 in. A clamp with a range up to 5/8 in. should be fine.
Quote
CTFSHJOHN
thank you .