Generac 20 kw Model 0058751 speed controler won't work after installing new Nexus controller. 
Quote
BillM
Someone is about to post here that they would like the serial number, and also could you give more information.  Like what lead you to replace the controller, symptoms, when it last worked, brief history, any other parts replaced, if you like hot or mild sauce on your taco's.  Basically more info will help.  Error codes .... LPG or NG, probably doesn't matter but why not?
Quote
Geoff Z
Thanks Bill M...I put this as a category how to get help from this forum. It rarely if ever gets used though. I'm going to add error codes to the list.

I'm a wimp and go with mild sauce!!!

Copy And Paste the following into your post:
Model #:
Serial #:
Total run hours:
Fuel source: NG or LP:
Length of fuel run:
Diameter of fuel pipe:
Last maintenance date:
Last valve adjustment date:
Last battery replacement date:
Quote
Daniel New
20 KW 2012 Model 0058751 installed 2013
Serial 6511820
LP
Last valve adjustment date -none
last battery replacement-1 yr.
Had to replace controller because only 10 volts going back to transfer switch and would not switch solenoid - had to have 12 volts. Fuel information is not an issue, been running fine sense 2013. It will run fine now if I manually advance speed at right side air cleaner. It just doesn't adjust on its own. 
Quote
78buckshot
Sounds like the stepper motor is bad OR the connector is not making contact at the controller. You can check the condition of the stepper if you have an ohm meter, get back to us and we'll lead you through it. Mild sauce for me too, and gluten free.
Quote
Daniel New
Ok how do I check stepper motor and or controller contacts?
Quote
78buckshot
Unplug the stepper from the control, at the connector you have 5 wires, measure the resistance from red to each of the others one at a time, should see in the neighborhood of 10 ohms on each, then check from each to the metal case of the stepper motor, you should see NO continuity. Be gentle with the connector as not to damage the female sockets. I also move the motor arm and re-check looking for the same results. On the controller you will see the five pins that make contact with the plug, inspect those pins for damage.
Quote
Daniel New
Thanks !  Checked 5 wire plug on controller and it was not fully inserted. Checked again and runs like it is suppose too. After thinking about it I was ready to put old controller back in and try it but when I saw 5 wire plug partially plugged - problem solved. Thanks again - keeping hopes up that when power goes off 12 volts will be sent to transfer switch.  
New to this forum stuff as you can tell. No comment on sauce or Gluten. Have a great Day.
Daniel 
Quote
78buckshot
Thank you for updating, it helps with answers on the post when folks are searching.