KennyB
Maybe I'm the only one interested in using the GFCI. I have a use for it when run in manual or exercise mode.
Quote
KennyB
One additional clarification to my question. Should the GFCI outlet have power when generator run in manual or exercise and power is NOT transferred to the house?
Quote
restosud
yes.it has power whenever the generator runs.volts and hz will be low if you're using quiet exercise though.
Quote
KennyB
Thanks restosud! Turns out the GFCI was tripped. I had tried to reset it, but generator was not running when I did this. Generator needed to be running to reset the GFCI outlet. Doh!
Quote