Will the RTSW200A3 transfer switch work with the older 15KW (2005) generator? I see that all the newer generators have 5 control wires whereas my generator only uses 4. Is this a problem or will it work with just the 4?
Quote
UPS
jallis;n58519 wrote:
Will the RTSW200A3 transfer switch work with the older 15KW (2005) generator? I see that all the newer generators have 5 control wires whereas my generator only uses 4. Is this a problem or will it work with just the 4?


The wire not used should be the T1 wire, needed only by newer generators to power the built-in battery charger.
Quote