lweford
I recently purchased a used 20kw Generac air cooled unit. This unit is going to be used on natural gas. I am wanting to replace the flex hose with the newer stainless flex hose. I am seeing 3/4 and 1/2” hoses. The original hose is 1/2” and the female port on the inlet at generator is 1/2”. Will the 1/2” stainless hose hose be okay? Keep in mind I will have 1-1/4” black pipe running all the way to the flex hose.
Quote
78buckshot
If you can find a 3/4"CSS line with 1/2" fittings it would be better, or a 3/4 x 1/2 reducing coupler at the generator inlet and use the 3/4 CSS line, the less restriction you can provide the better, same with any shut-off valve you might be using - bigger is better.
Quote
lweford
So I have a 1-1/4” full flow shutoff valve. Every part of my 15’ gas run is 1-1/4” except for the 1-1/4” x 1/2” reducer and the flex hose. So I will have approximately 12-15 inches(flex hose and short nipple) of 1/2” gas line in my run and that will be right at the generator. I just don’t want any fuel issues.
Quote
Birken Vogt
I've seen some pretty awful installations like 1/2" pipe running 50 feet which goes negative when it starts but the thing still works like that.  A few feet of 1/2 is not going to bother anything.  If it has a 1/2" inlet then it is meant to run like that.
Quote
lweford
Appreciate the info. Just want to have things done right the first time.
Quote
78buckshot
Looks like your good to go.
Quote
Brian Baughman
Everything will be fine, just be sure to follow the installation instructions on the Dormont label.
Quote
restosud
lweford wrote:
I recently purchased a used 20kw Generac air cooled unit. This unit is going to be used on natural gas. I am wanting to replace the flex hose with the newer stainless flex hose. I am seeing 3/4 and 1/2” hoses. The original hose is 1/2” and the female port on the inlet at generator is 1/2”. Will the 1/2” stainless hose hose be okay? Keep in mind I will have 1-1/4” black pipe running all the way to the flex hose.


re check the inlet port on generator.the thread should be 3/4"npt and 20kw's came with a 3/4" threaded black rubber flex hose
Quote
lweford
Yeah I have checked again and it is 1/2" npt. I even had the fuel system recall done after I purchased it, which essentially is a totally new fuel system, and the inlet on the new system is 1/2" npt as well. I don't know. The dealer said 1/2" is enough and a couple of you guys said it would be fine as well so I am gonna go with it. All I know is my Rinnai on demand water heater has a 3/4" inlet for NG and it's only 199,999 BTU. 
Quote
78buckshot
Whatever the engineer deemed adequate for each application, as long as you have followed the piping charts for the unit you'll be good.
Quote
restosud
can you post a pic of the inlet and the model and serial number?
Quote
lweford
Thanks Geoff Z. Looks like I will be contacting the dealer who did the recall. Looks like they installed the wrong inlet. I don't have a shot of the inlet right now.  
IMG_0605.jpeg 
Quote
Geoff Z
I looked up your installation manual using your serial number. Your model is a 1/2” inlet. The other was from today’s installation manual. I wouldn’t have thought that would change. Forgive the misinformation. 
Quote
lweford
Appreciate you doing that. Glad to figure it out before I called them in the tomorrow morning. 🙂 What I did was put a 1/2npt x 2" nipple in the inlet with a 3/4npt x 1/2npt reducer immediately afterwards. Now I can use a new steel 3/4 flex hose to my run of 1-1/4npt.
Quote
Mike03
Ideally you should have used half inch shoulder nip into a 3/4"x1/2" black tee for your sediment trap. And came off the top of tee with 3/4" 90 and you 3/4" flex hose.
Quote
Geoff Z
Yes that generator does not have a built in sediment trap. Whereas today's air cooled models do.
Quote
lweford
I can always put one right next to the input of the generator but I do have a sediment trap about 5’ upstream in the 1-1/4” section of my run.
Quote
Wireform
lweford wrote:
I can always put one right next to the input of the generator but I do have a sediment trap about 5’ upstream in the 1-1/4” section of my run.
Would love to see a picture of that trap as half the time they don't work in the configuration they're installed. It's not a magic kind of thing that the sediment falls into the drip leg so what you have there may not be doing the job