Finally have the unit running and charging but now something is draining battery and when I set unit exersize time it starts but does not shut down after it runs a while, when I shut it down manually and set switch to auto the unit starts after approximately15 seconds.

Any ideas?

Thanks.
Quote
Peddler
What is the green light doing on the control panel when you put it auto? Also check the function of the set exerciser switch with an ohm meter.
Quote
78buckshot
Check for 120 volts on N1 to ground and N2 to ground, 240 volts N1 to N2 at the generator. If you don't have both lines hot the unit thinks utility has been lost and you wont have battery charge input.
Quote
rapidroy5858
Found the 1 5 amp fuse bad in transfer switch. Will buy a new fuse and install and see if auto / excersize function works properly.