durell johnson
can anyone help me with a 22kw it is no reducing any power
Quote
78buckshot
Did the unit shut down and latch on "under voltage"? Where have you checked for output?
Quote
durell johnson
from the phases in generator and also the gfci receptacle  in the generator no voltage was accur 
Quote
78buckshot
If you are sure you checked on the generator side of the MLCB and have no output then the next step is to check the resistance in the rotor circuit. Disconnect the wiring harness plugs from the controller and find wire #4 and #0(zero) that lead to the brushes. Resistance through the harness, brushes and slip rings should be 18 - 22 ohms. If you turn the rotor/engine and get wild fluctuations in the readings it's time to clean the slip rings and center the brush holder.
Quote