Has anyone come across the surge capability for the new 10kw and 13kw models? I haven't seen a new sizing guide since the release of the new model lineup.
Quote
Geoff Z
I have asked and it is not available yet. I'm going to check again.
Quote
Geoff Z

New sizing guide is not out yet. Here are the values we were given:

10kW: LRA at 30% voltage dip 70A

13kW : LRA at 30% voltage dip 95A

16kW : LRA at 30% voltage dip 130A

I am surprised at the 13kW value. The previous 11kW was rated at 92A running a 530cc on natural gas which makes it a 10kW. The new 13kW is a 816cc which is 13kW natural gas or propane. We go up to 95A. 3A increase does not seem correct to me. One value or the other has to be wrong.

Quote
BrianMartin
I assumed the figure for the 13Kw would be much closer to the 16Kw's. I guess we will see once they put it on paper. Thanks for getting those numbers Geoff. 