Hi Guys
I purchased separate 1/0 aluminum service wire for the power between generator and the transfer switch. 
However, I still need to buy the control wire for the same. I understand, majority of the folks use single cable for both power and control, however I already had the pre-wired 1/0 in the house that I want to utilize.
can someone please confirm what exact control wire do i need to use along the 1/0 cable to install the generator ?
Distance between unit and the transfer switch is 100ft.
Will this be a 16/6 awg conductor wire OR 16/8 awg conductor wire 600V?

appreciate the help.

Zack
Quote
BillM
The installation manual says all you need is 18 AWG for a run up to 115 feet.  You need 6 wires.
Quote
BillM
The installation manual states 18 AWG is all that is needed for up to 115ft.  It will be 6 wires.  You can download the installation manual and in my manual, it's section 6-2 of the manual..... titled;  Control Wiring
Quote
zack
Thank you BillM !
Quote
Cobranut
Look up "tray cable".
It's available in many gauges and conductors, is approved for installation in conduit, and is reasonably priced. 
Quote
78buckshot
Zack, yes you need 600 volt rated conductors, three of them will carry 120 vac, the other three are 12 vdc.
Quote
zack
Thank you Guys for the help. Much appreciate it. 
Quote
Geoff Z
Moved topic to Installation Talk, Combined post from BillM, deleted duplicate topic
Quote
Brian Baughman
The generator control conductors are Class 1 circuits.  The NEC and Generac installation manual require that Class 1 circuits be wired with NEC Chapter 3 wiring methods.  The use of sprinkler control wiring, or thermostat wiring, or any other Class 2 wiring method is prohibited.  The best option is listed Type TC-ER-JP, but Type UF cable can also be used.
Quote
Geoff Z
You can also use #16 THWN in a raceway