kmyers57
Can someone post a pic of where I can land our wires to extend the Modbus rs485 circuit ? We have to bring the Modbus into a BAS ( building automation system) at (4) remote VA clinics. I called Generac Tech support and was told the terminals are in the "Customer connection panel". I'm not famliar with these generators and have opened every access door on the genset looking for the connection panel. The literature that we were given by the VA is for the H-100 panel and doesn't show the connection panel just programming details.
thanks
Kevin
Quote
ceb58
kmyers57;8510 wrote:
Can someone post a pic of where I can land our wires to extend the Modbus rs485 circuit ? We have to bring the Modbus into a BAS ( building automation system) at (4) remote VA clinics. I called Generac Tech support and was told the terminals are in the "Customer connection panel". I'm not famliar with these generators and have opened every access door on the genset looking for the connection panel. The literature that we were given by the VA is for the H-100 panel and doesn't show the connection panel just programming details.
thanks
Kevin


Not sure what size you have but most of mine are inside the enclosure on the end of the gen. that the armature is on. You remove the 8-10 bolts on the cover to expose the amateur There is a terminal strip there for the connection of the start wire. Those connections are along that strip. PITA to get to. The strip will fold out some but you still have to stand on your head.