The Mobile Link seems to work well from what I can see so far but just wondering why they don't give you a little more control on the app such as the option to control the Auto-Manual and Off on the controller ? Thinking it might be handy.
Quote
Cobranut
The Mobile Link seems to work well from what I can see so far but just wondering why they don't give you a little more control on the app such as the option to control the Auto-Manual and Off on the controller ? Thinking it might be handy.


Because without additional equipment you cannot remove the load from the generator before shutting it down during an outage.
Quote
Sherwooddavid

Ok thanks Cobranut. 

If you turn off the auxiliary shutdown switch does that remove the load first ? Just wondering. Thanks

Quote
JayH

Ok thanks Cobranut. 

If you turn off the auxiliary shutdown switch does that remove the load first ? Just wondering. Thanks



It does not. It just immediately shuts down the engine. There really isn't an easy way within the generator to remove the load other than manually flipping the MLCB.
Quote
Cobranut

Ok thanks Cobranut. 

If you turn off the auxiliary shutdown switch does that remove the load first ? Just wondering. Thanks



Nope.  At that point they assume your house is ON FIRE, and damaging the genset or your A/C compressor is not so important. LOL