Hi everyone installed a 16 kw generator and had it hooked up green lite is on and panel says ready to go.. Electrician went thru all the tests everything worked 2 questions
   1. have it set to exercise once every two weeks.. I am in NJ good choice or is once a week better?

    2, The start up draw on the one AC unit was determined too much for the 16kw I installed and rather than install a smart start on the compressor decided since power loss in summer is almost non existent I decided it was easirer for now to lock out AC unit If stand by ( generator) power goes on..  reading up on it was easier to not go up in attic to the air handler and just go from Transfer switch to thermostat wire in compressor ... So did I do this correctly?? Ran two wire thermostat wire from AC1 in Transfer Switch and ran it to compressor unit where I wire nutted it to where thermostat wire from house came in ???? See pics
ac1.jpg 

AC 2.jpg 
Quote
78buckshot
I can't see the wiring well enough at your ac condenser but it looks like you did not interrupt the thermostat signal. What size is the ac system? Did your electrician wire the transfer switch as a 'whole house' transfer?, if so then you did not lock out the ac, you have it on 'load shed'.
Quote
bikerboy108
What is Load Shed ??   yes transfer switch is a whole house transfer switch ... we ran the "Brown" 2 wire therm wire from the transfer switch over to the compressor and wire nutted it to the "curly white" therm wire that comes from the house thermostat that controls the AC ...  

So is the connection to the transfer switch in the wrong spot?? Below in Italics was what I was trying to do???

If it is easier to run the wire outdoors to the condenser. Pull the disconnect to the unit to kill the 240 power source. Look for the high voltage contactor. It should have low voltage control wires to a 24v coil. Identify which is the 24v hot and disconnect it. Connect this wire to one from the nexus smart switch. Connect the other wire from the smart switch back to the contactor. All you want to do it put the switch of the nexus in series with the control wires.


AC4.jpg 
Quote
78buckshot
Load shed allows the ac to run if the generator can handle the load, so if the rest of the house is not using much energy then the ac can run, if the generator is near capacity and the ac tries to start the controller will sense a drop in engine speed and won't allow the ac to run. If you can separate the yellow control wires a little more and send a new picture I might be able to give more info. Leave the wiring as is in the transfer switch.
Quote
bikerboy108
whole reason was the LRA on AC was 169 and 16kw generac couldn't handle that so easiest way I was told is either smart control.. or just eliminate it.. Hope these pics help    white therm wire from house ..brown from transfer switc
ac6.jpg  AC7.jpg     AC10.jpg 
AC7.jpg 
AC8.jpg 
Quote
bikerboy108
I think the 16kw can only take 130 LRA ??? Not sure

If it is easier to run the wire outdoors to the condenser. Pull the disconnect to the unit to kill the 240 power source. Look for the high voltage contactor. It should have low voltage control wires to a 24v coil. Identify which is the 24v hot and disconnect it. Connect this wire to one from the nexus smart switch. Connect the other wire from the smart switch back to the contactor. All you want to do it put the switch of the nexus in series with the control wires.
Quote
Birken Vogt
If you absolutely do not want the AC to run you could slave a contact on the side of the transfer switch mechanism instead of the computer controlled load shed you are using.

The 16kw has a bit of an oversized engine though so it might be able to start this large AC anyway.  I would try it out in the summer as-is and see how it does before changing to the slave contact method.
Quote
Geoff Z
I think the load is simply too big. Should consider either a Sure Start on it or take it off the generator. There might even be a chance the generator could start it with no other load connected. However imho setting the system up for nuisance issues. For each time the SACM activates it must see a frequency drop to do so. Keep in mind everything else being simultaneously powered by the generator will be subject to that same frequency drop. Not good. There already is an auxiliary contact on the side of the transfer mechanism. Wire the switch leg to the run relay through that NC contact and done.
Quote
78buckshot
Thanks for the wiring picture, you have it wired correctly for load shed however I would not run the ac on generator due to the tonnage - appears to be a 5 ton system, so either a SMM or do as Birken Vogt says and use a limit switch on the transfer mechanism.
Quote
UPS
bikerboy108 wrote:
whole reason was the LRA on AC was 169 and 16kw generac couldn't handle that so easiest way I was told is either smart control.. or just eliminate it.. Hope these pics help    white therm wire from house ..brown from transfer switch


Are you sure the white wire where you made the new connection is directly from the thermostat?  Generally the thermostat is wired to the air handler with 3 to 5 wire cable so it can control the blower fan and also the heat if a combined system.  A 2 wire cable then runs from the air handler to the compressor contactor.  If what is being locked out here is only the compressor, then if it is warm enough for the thermostat to be calling for cooling, the blower fan will run continuously.
Quote
bikerboy108
UPS wrote:


Are you sure the white wire where you made the new connection is directly from the thermostat?  Generally the thermostat is wired to the air handler with 3 to 5 wire cable so it can control the blower fan and also the heat if a combined system.  A 2 wire cable then runs from the air handler to the compressor contactor.  If what is being locked out here is only the compressor, then if it is warm enough for the thermostat to be calling for cooling, the blower fan will run continuously.


 You are probably right white wire comes from air handler


Geoff Z wrote:
I think the load is simply too big. Should consider either a Sure Start on it or take it off the generator. There might even be a chance the generator could start it with no other load connected. However imho setting the system up for nuisance issues. For each time the SACM activates it must see a frequency drop to do so. Keep in mind everything else being simultaneously powered by the generator will be subject to that same frequency drop. Not good. There already is an auxiliary contact on the side of the transfer mechanism. Wire the switch leg to the run relay through that NC contact and done.
Geoff Z wrote:
I think the load is simply too big. Should consider either a Sure Start on it or take it off the generator. There might even be a chance the generator could start it with no other load connected. However imho setting the system up for nuisance issues. For each time the SACM activates it must see a frequency drop to do so. Keep in mind everything else being simultaneously powered by the generator will be subject to that same frequency drop. Not good. There already is an auxiliary contact on the side of the transfer mechanism. Wire the switch leg to the run relay through that NC contact and done.


There already is an auxiliary contact on the side of the transfer mechanism. Wire the switch leg to the run relay through that NC contact and done

Geoff
#1  I answered UPS Above does that affect you answer?
#2  Your answer is greek to me will my electrician understand that?
     
Quote
Geoff Z
Sorry I should have been more clear. The two wires you have terminated on the SACM will simply be removed from there and terminated on the auxiliary contact. That contact will be normally closed (NC) while on utility power allowing the A/C to run. On generator power that contact will open disabling the A/C.
Quote
Geoff Z
I also meant to confirm that you are correct that the 16kw is rated for 130LRA. Once we begin to introduce other loads on the generator that 130LRA capability begins to diminish. The more other load on the generator the less LRA motor start is available. If you decide to try and start it in the summer revisit this thread and let us know how it goes. I would be really interested to hear the result.
Quote
78buckshot
From the model info on the condenser plate it looks like a 5 ton ac system, the 16kw will struggle to start it if it can do it at all, my 15kw labors to start my 3 ton if I take all of the other loads off - I don't have a soft start.
Quote
murphy
78buckshot wrote:
From the model info on the condenser plate it looks like a 5 ton ac system, the 16kw will struggle to start it if it can do it at all, my 15kw labors to start my 3 ton if I take all of the other loads off - I don't have a soft start.


Have the capacitors in your compressor cabinet been tested recently?  The last one I changed had dropped from 45 mfd to 0.7 mfd.  That greatly increases the starting current.  My old 7 kW generator could easily start my 3 ton compressor after I installed a soft start unit.  It reduced the starting current from 79 amps to 45 amps.