rico567
Model #: 5871, 10KW Serial #: (? )
Propane or Natural Gas:Propane
Length of gas pipe feeding the generator: @ 50 ft.
Size of gas pipe feeding the generator: ?
How long since the last full maintenance: September 2016
How long have you experienced this problem:today 4/24/17

Description of problem: Checked generator, showed red light. Display read "overspeed."

Steps you have taken to resolve problem:

1. Reset by turning to "off."
2. Did manual start. Unit ran for 30 seconds, shut down and returned "overvoltage" error.
3. Repeated steps 2 & 3 with same result.
4. Reset generator, set to "auto."
Quote
Peddler
You need to check frequency as the unit may simply be running fast which would also cause an over voltage. Make sure the governor is maintaining 60Hz. Peddler
Quote
Ziller Tech
In any case, resetting it and putting back in 'auto' is not a good idea if something is really wrong and for some reason you lose power. You don't want there to be a chance that the generator would be connected to the loads in the house like that.
Quote
rico567
Thanks for the replies. I will set the unit to "off" until I can figure out what's going on.
Quote
nrp3
Could it be the stepper motor is either unplugged or just not functioning?
Quote
MikeCB
What region are you in? Are there signs of bugs and ants having gotten into the control board? I see a lot of problems with ants this time of year, they are attracted by warmth of electronics. They get in there and confuse the computer, voltage regulator, or both.
Quote
rico567
MikeCB;46051 wrote:
What region are you in? Are there signs of bugs and ants having gotten into the control board? I see a lot of problems with ants this time of year, they are attracted by warmth of electronics. They get in there and confuse the computer, voltage regulator, or both.


Uh-oh! When I was looking at the display to check out what was wrong, lots of tiny ants crawling around in behind the display screen. I'll have to take care of those guys......
Quote
Ziller Tech
rico567;46053 wrote:
Uh-oh! When I was looking at the display to check out what was wrong, lots of tiny ants crawling around in behind the display screen. I'll have to take care of those guys......


They may have already taken care of you... :(
Quote
kershner
Thanks guys for the new "what to prepare for". Spring: add an insecticide around the base. Winter: Put a guard at the rear to keep generator cooling open. Fall: Put a small mesh fence around air intake end to keep leaves off the intake. Looking forward to something to do for summer. This is great forum and I have learned s lot. Thanks for taking time out of your busy days to share.


Sent from my iPhone using Tapatalk
Quote
MikeCB
rico567;46053 wrote:
Uh-oh! When I was looking at the display to check out what was wrong, lots of tiny ants crawling around in behind the display screen. I'll have to take care of those guys......


Damn, was hoping my hunch was wrong. Sorry.

I keep a toothbrush in my bag and am often lucky enough to brush them away and restore function. It all depends on whether or not they damaged one of the controller components, or are just confusing it. Keep in mind though, and I always tell my customers, that reliability is NEVER guaranteed once they have gotten in there.

Check the above mentioned engine speed issues before you go replacing the controller (it's not cheap). But if you truly were having speed issues you would most likely see an "overspeed" instead.
Quote
Hodgy
.

Wow our generators are susceptible to ants.

"The average ant can actually carry up to 50 times it's body weight, and some ants can lift an incredible 100 times their body weight !"


We will all be long dead and there will still be insects on this planet.


.
Quote
MEC
Yep, seen that quite a few times.

Usually pull it and open it up to vacuum them all out and then reverse and blow out all the rest. Little diatomaceous earth and hope for the best.
Sometimes it's a lost cause because the damage was already done.


Sent from my iPad using Tapatalk
Quote
EbaYau
rico567;46033 wrote:
Steps you have taken to resolve problem:

1. Reset by turning to "off."
2. Did manual start. Unit ran for 30 seconds, shut down and returned "overvoltage" error.
3. Repeated steps 2 & 3 with same result.
4. Reset generator, set to "auto."


Hi...i am a new user here. As per my knowledge resetting it and putting back in auto is not a good idea if something is really wrong and for some reason you lose power. You don't want there to be a chance that the generator would be connected to the loads in the house like that.