I'm installing a Generac 10 kw with nexus controller. Have approx. a 25 foot straight run of 3/4 inch gas line that is currently shared with furnace, stove, clothes dryer, and during the summer I have a gas grill connected on the end of the run on the outside of the home. Can I connect a "T" fitting on the end of the run (where I connect the grill), carry it around the corner of the house approx. 5 more feet of run, and still have enough gas to run the generator? Minimum requirement is 6 inches of water column. Thanks
Quote
Skip Douglas SkipD
First off, you may need to up-size the meter and regulator for your house. Add up all of the consumption figures for all of the appliances presently connected. Then, add the consumption of the generator (at 100% load). Compare the total to the figure on the meter/regulator. If the total you calculated is larger than the rating of the meter, you will need to contact the utility and get a new meter installed.

THEN, you should calculate the pipe size required based on the device(s) at the other end of the pipe. [url=http://www.propane-generators.com/natural-gas-chart.htm][COLOR=Blue][U]This Natural Gas Pipe Chart web site[/U][/COLOR][/url] can be a big help in doing the necessary calculations.

My guess is that the pipe you presently have will not be large enough for the task and you will probably need a new meter.
Skip Douglas
Quote
ohmslaw
The gas line just makes it for a 10 kw with out any other loads. The answer is no.
Tim
Quote
spider60
OK...thanks for the advice. PW