I have a Generac PowerPact™ 7.5kW Model 6998 generator that the choke butterfly has started sticking in the closed position. The generator is about 8 months old and worked fine until a week ago. I can take my finger and touch the butterfly and it pops right open. Is there an adjustment on the choke system? Any ideas how to fix this will be appreciated.
Quote
nrp3
Usually, there is a range of adjustment on the mechanism itself, a slot that you can adjust the position of the solenoid. I had to replace one of these on a powerpact recently for the same thing. It could get stuck closed or open. Similar problems could occur with the Nexus and older 10kw units. I typically replace them. If I recall it would also happen on the Corepower, it's predecessor.
Quote
ozark01
nrp3;52462 wrote:
Usually, there is a range of adjustment on the mechanism itself, a slot that you can adjust the position of the solenoid. I had to replace one of these on a powerpact recently for the same thing. It could get stuck closed or open. Similar problems could occur with the Nexus and older 10kw units. I typically replace them. If I recall it would also happen on the Corepower, it's predecessor.


Do you by chance remember the part number of the solenoid?
Quote
JoeL
what is the serial # on this generator
Quote
nrp3
Probably still under warranty, think those had two years.
Quote
ozark01
JoeL;52464 wrote:
what is the serial # on this generator


The serial number is 3001696379. Thanks!
Quote
JoeL
choke solenoid part # is 0f9273 it is $ 42.75 on Zillers online parts store.

This generator is still under full warranty, parts and labor at no cost to you.

Contact an Authorized service dealer, you can find a dealer locator on Generacs home page
Quote
ozark01
JoeL;52469 wrote:
choke solenoid part # is 0f9273 it is $ 42.75 on Zillers online parts store.

This generator is still under full warranty, parts and labor at no cost to you.

Contact an Authorized service dealer, you can find a dealer locator on Generacs home page


ok....thanks for the info!