I am installing a Generac 5875 20kW generator. The local utility will be installing a new meter and line from the gas main which is about 15 feet from the generator installation location. I assume I will have to make sure they install a regulator on the meter that regulates to between 5" and 7" water column as specified in the installation manual? The generator will be the only appliance on this new meter (the rest of the house is on a separate meter coming from a separate line off the main gas line)

The length of pipe from the newly-installed meter to the generator is about 8 feet and includes 2 elbows. The size of the gas line input into the generator is 1/2", and it comes with a flexible hose that is also 1/2" in diameter. In reading the manual it appears however that I need to run at least 1" pipe from the meter to the generator. Is that correct, even though it is only 8 feet of pipe? If not, then does that mean I can run 1/2" pipe from the generator to the meter, then upsize to 1" so that it can connect into the meter? If if I have to use 1" pipe from the meter, then I guess I would need to reduce the 1" pipe from the meter to 1/2" so I could connect to the flexible hose and then connect into the generator itself? Is that correct? Sorry for the seemingly dumb questions, just want to make sure I am figuring this correctly.

One last silly question: if I do have to run 1" pipe up to the flexible hose, doesn't the 1/2" diameter limit the gas flow at the point of connection, so that I am not getting the "full flow" of the 1" pipe?

Thanks in advance for your answers.

Steve
Quote
Skip Douglas SkipD
You need to run the larger diameter pipe for as much of the run as possible. You may find [url=http://www.propane-generators.com/natural-gas-chart.htm][U][COLOR=Blue]this link to a pipe sizing chart[/COLOR][/U][/url] quite handy.
Skip Douglas
Quote
americast precast genslab
Installers: Please be advised of the following pre-cast gen pads.You can now install your generators with this specifically engineered Pre Cast Gen Pad with 1 trip to the job site and a price tag of f $130.00 for the Gen Pad.
Your Generator, Our Pad, One Trip to the Job site:
AMEricast Tel. 772-971-1958 [url]www.ameri-casting.com[/url]
GEN PADS 7kw--30kw
$130.00 Includes Delivery USA

Gen Pads $130 Order of 10=$1300 ($130per pad)

Order of 5==$800 ($160 per pad)
Order of 4==$720 ($180 per pad)
Order of 3==$600 ($200 per pad)
Order of 2==$450 ($225 per pad)
Order of 1==$250 ($250 per pad)
Includes Engineering & Delivery USA
These Pads Accommodate:
Generac 7 kw - 20kw Pad Weight 200 LBS
Generac 22kw - 30kw Pad Weight 250 LBS
No pouring in place.
Our Single Pads can handle 7kw to 60kw
Single Pads 54" x 32" x 4" 8kw to 20kw Wt. 200
Single Pads 68" x 35" x 4" 22kw to 30kw Wt. 250 lbs

Super Single: 84"x 42" x 4" 36kw to 60kw Wt. 430 lbs
Quote
americast precast genslab
installation

Installers: Please be advised of the following pre-cast gen pads.You can now install your generators with this specifically engineered Pre Cast Gen Pad with 1 trip to the job site and a price tag of f $130.00 for the Gen Pad.
Your Generator, Our Pad, One Trip to the Job site:
AMEricast Tel. 772-971-1958 [url]www.ameri-casting.com[/url]
GEN PADS 7kw--30kw
$130.00 Includes Delivery USA

Gen Pads $130 Order of 10=$1300 ($130per pad)

Order of 5==$800 ($160 per pad)
Order of 4==$720 ($180 per pad)
Order of 3==$600 ($200 per pad)
Order of 2==$450 ($225 per pad)
Order of 1==$250 ($250 per pad)
Includes Engineering & Delivery USA
These Pads Accommodate:
Generac 7 kw - 20kw Pad Weight 200 LBS
Generac 22kw - 30kw Pad Weight 250 LBS
No pouring in place.
Our Single Pads can handle 7kw to 60kw
Single Pads 54" x 32" x 4" 8kw to 20kw Wt. 200
Single Pads 68" x 35" x 4" 22kw to 30kw Wt. 250 lbs

Super Single: 84"x 42" x 4" 36kw to 60kw Wt. 430 lbs
Quote