d11gnccer
Carrier model: 0053130
Serial: 3007V24542
45KW 2.4L mitsibishi


I was sent to a call 40 miles above our typical service area because the customer could not find anyone to service unit.

Generator will crank but no spark is present and goes into a flashing overspeed lockout. From what I can gather the controller doesn't see the engine cranking. I was on tech support with Generac but found it difficult to stand in the rain, up to knees in mud, with a phone that had minimal service in one hand, and multimeter leads in the other. They was pointing me to flywheel sensor and cam sensor. At that time I didn't even know where they were located and was frustrated.

Any input on what type of readings I should be getting or how to systematically approach the problem. No diagnostic manual could be found under generac website.
Quote
d11gnccer
Just to add some information as I learn and go in case someone does a search later on.

Original sensor reading was 1.8 volts which I was told is a little high.
The flywheel sensor should give a reading of 1-1.5 volts on pin 9 and 10.
Ohm readings on these sensors are around 1000. After replacing control board and pulling sensor to clean magnet and adjusting to get 1.2 volts output, board still flashes overspeed. Took a look at the cam sensor for after getting an open circuit ohm reading. The end was chopped off and frayed wires protruding from end of sensor. The cam sensor should be set at .015"

We are ordering a cam sensor and will see if this solves the problem.
Quote
Geoff Z
This is going to take care of your problem. I've seen it numerous times. Be very careful replacing that sensor!
Quote
ehelectric
Replacing cam magnetic pickup

What is the trick to replacing this and what voltage should i read when correctly installed. Is that also 1.2 volts like the flywheel sensor? Any help would be great got a customer stuck with no power. Sorry it is the 35 kw 2.4 L mitsub. Model 0052621, ser. 4636905.
Quote
douglas123
Let me pull up your model. If you are talking about mag pick up on flywheel adapter make sure tooth of flywheel is in the center of the hole and screw mag in until touches tooth and back out at least one full turn to be on the safe side. try to start unit if it does not screw in just a litle bit unit it does and take a reading with your meter. will post specifics asap.
Quote
ehelectric
cam sensor

No, I have replaced quite a few of the flywheel sensors. This one is located on the engine and is like a cam sensor(rpm) maybe. Looks identical to the flywheel sensor but has a different part number. Looks like a nightmare to change.
Quote
douglas123
Ok Pullep UP the service pages you need. Just need to scan and E-mail them to you. Send me your E-mail address And I will get them to you ASAP. Scanning now.
Quote
ehelectric
Thanks!

mail at ehelectric dot net or sheaney4 at gmail dot com

You are a lifesaver!



From moderator:

Folks, it's a very bad idea to embed actual email addresses in forum messages. You can turn on the feature that allows forum members to email you through the forum software, and that hides your email address from the spammers looking for them. You can also Private Message other members with your email address(es) if you wish.