Doing an installation with 2 transfer switches. Can the lugs on the transfer switch supplying power from the generator be double tapped to provide a paralleled connection to the other transfer switch. Need to know if they are rated for that?
Quote
Brian Baughman
The lugs on the Generac 50-200A transfer switches are only listed for one conductor per lug, 300A and 400A transfer switches have lugs that are listed for 2 conductors per lug.
Quote
MacL
We use Polaris lugs 
State your problem, not your diagnosis.