Hey gang I wanted to install a battery and oil filter heater to my carrier, can that be wired to n1 and n2 or does that need another circuit? 20180926_161356.jpg 
Quote
Peddler
Best to put it on a seperate circuit.  
Quote
Blaze
Thanks peddler
Quote
BillM
I have the Generac supplied heaters and they connect to N1/N2.  I ran ethernet and alarm contact wire to my generator, but never thought of running a separate circuit out there and regret not doing so.  My next install is going to have the ethernet, alarm wiring AND a 20 amp circuit out there.  #SAD
Quote
Blaze
What is the current draw of the battery and oil filter heaters?
Quote
grsthegreat
East take aprox 40-50 watts, 240 volts. Newer units run off of fused N1 and N2, but having separate circuits are nicer because if the unit shorts out the circuit supplying it, the generator won’t false start 