Hi guys,

Is there a quick and easy way to test the battery charger regardless of model, at the battery connection? 
Quote
Wireform
I guess if you put a meter to it when the gen is off and see what the reading is at the battery. Not sure but should be 13.8 or so. I f it were just reading the battery it'll be maybe 12.3 at the most.
Quote
78buckshot
With the battery charging you will see 13.2 - 14.2 volts DC at the battery depending on temperature, model of generator. If it's below 13.0 volts or above 14.5 volts you need to diagnose why.