2016 8KW with ATS. After lighting storm both N1, N2 fuses blown. Replace fuses reset Gen to auto and says utility loss and starts. check voltage all the way from fuse block to controller. I have 230V going into controller. Everything is functioning correctly. Manual works, the ATS is working but when put in auto it starts. Seems to be the controller any thoughts?
Quote
78buckshot
 I would say the lightning also damaged the controller, if you have 230 volts into the control and it thinks you lost power it got hit.
Quote
Dick from Canada
Took lightning strike once. A flash and a crack . Turned on every alarm on the controller. Reset it and everything worked, Lucky for sure !
Quote
Peddler
You could try a reboot but I would guess the controller took a hit.
Quote
C H
Thanks for the input do believe it's the controller but wanted to bounce it off others before buying another controller. Not cheap.

Thanks
Quote
grsthegreat
Did you try a reboot yet. Unplug 130 power to controller and unhook battery ground. Wait 30 seconds and reinstall all. Couldnt hurt.