I have a 7kw that started automatically last nite but failed to shut down when utility power was restored, had to shut down manually.
anyone have an idea???
Quote
douglas123
I little more info on model and serial number of generator and what transfer switch you have woud be most helpful is getting you the correct answer to your question. Did you put your generator back in auto after you manually shut it off and did it try to restart or not?
Quote
sborruso
7kw failed to shut down

model 0052510 serial 4393283 it started when switched to manual mode and didn't try to start when switched to auto, not sure what transfer switch is in it, read something about a cooldown timer?
Quote
douglas123
upon power outage there will be 10 seconds before the unit starts. 15 seconds later it will initiate a transfer to emergency assuming voltage and hz are correct. Upon restoration of utility power the unit will transfer back to normal utility power source in 15 seconds and run approx. a 1 minute cooldown and shut itself off. Any further run time with unit on energency and utility power restored might have blown sensing fuse in transfer switch or power is not back at proper voltage or you do not have both phases fully restored. need any more assistance please ask.