MODEL 0521 20 kw 1.5L LP GAS
Runs rough , Heavy smell of LP when running
output is good 244v with load 60hz
Quote
Scotty306134
Assuming normal compression it's either getting too much fuel, the air filter is clogged, it's running with the choke closed, fuel inlet pressure is too high or the ignition sys is breaking down.
Quote
bronco
Try turning the fuel shutoff while its running. If you are getting to much fuel as you close the valve the unit will run better.
Quote
hoghead
Unit was installed in 2006,was never converted to LP {regulator and dip switch}
W.C. was 10"
generator runs great now.
The original call for service on this unit was it would not re-transfer after an outage.
Control wire was 6 conductor Thermostat cable with a high resistant short.