Lost power, unit started but did not transfer to house, manually shut it down, all warning lights lit and won't reset, breaker on unit kicked out .
Quote
Geoff Z
Our techs will be able to provide better input if you provide model and serial numbers
Quote
Haytch
serial # 5314517  model 0055010 , not sure if breaker was off or kicked.
Quote
george6488
Post under "air cooled" and many techs will see your question. Over here...not so much.
Quote
Geoff Z
I moved to Air Cooled. 
Quote
Peddler
Well if the breaker is tripped it will not transfer under any circumstances.  You say all the warning lights are off...Will the unit start in manual and will it continue to run.  All the lights flashing could mean it has lost its exercise program and nothing more.  If you put the switch in auto doe the green led come on.  IF so try setting the exercise and see if theat clears the flashing lights.  Then we'll need to see if it is producing power.
Quote
Haytch
Turned it off, reset the exercise program and it has been ok since, ---operator not to bright!