sean

Called in to service generator, had not been touched for 2 + yrs. working / running just fine, oil change , etc. when testing voltages,200 and 120-N. Both legs under load.  Ohms on wire 4-0 is 315 ohms, my guess is dirty slip rings ? Do you all agree before I tear down ? Model is 005050 Ser 5646734  17 kw generac

thank you
On the rock

Quote
78buckshot
If in fact you were measuring the resistance of the rings/brushes/rotor without any other component connected then yes, slip rings and/or brushes need attention. I'm a little confused on the voltage reading though, are you saying you had 200 VAC on one leg to neutral and 120 VAC on the other leg to neutral? After re-reading I see the title, I think that machine has a separate voltage regulator that has an adjustment pot, try turning it clockwise while the machine is running with your meter on the output.
Quote
sean
Ha, that was confusing, 200 volt phase to phase , 100 volt phase to neutral both phases.
Yes, it does have a voltage regulator with voltage adjust screw but I was a bit concerned to adjust until I find cause of voltage change. i will access slip rings and brush in the morning, polish rings, clean and inspect brushes , test and then run. Adjust regulator! Is this adjustment made periodically ? I have not needed to do this other than new imstallation.
thank you 
Quote
78buckshot
The regulators tend to "creep" as they age, most that I see go higher with time. I would certainly clean the slip rings and after you get it back together adjust the VR. With the age of it don't be surprised to find a very touchy pot, might have to replace the regulator if it won't stay.
Quote
sean
Can I get the part number for the AVR for this 17 kw please
Quote
78buckshot
You can call Ziller with your serial # and they can probably ship it out the same day.