Have 16kw Generac with only residual a/c output. Performed tests according to the A route on the flow sheet.After doing test 6- Check field boost, replaced voltage regulator, still no output. I did notice with gen in off position, I had 50 volts dc on wire #4, manual says it should be 0? Could the circuit board be bad as well?
Thanks for any help,
Adam
Quote
bronco
model and serial numbers?
Quote
adam
Bronco,
Thanks for the reply; I'm on duty for 24 hrs at fire station, I'll get the info when I get home and re-post.
Thanks,
Adam
Quote
adam
Bronco,
I got the generator back up and running. Had to ad an external field boost circuit. Disconnected the one from the circuit board. Running perfect now!