3 out of the last 4 units I have installed have had this code come up 1300 oil pressure one on an outage (tech came out replacing engine) second one first exercise cycle no go 1300 code, has had a tech out three time (suspected incorrect size switch 5 or 10 psi found loose wires on said switch Stated ok next exercise cycle no go next time out said software update required, Generac has claimed to update it 3 times next exercise no this unit has been installed for a little over 6 weeks (hasn’t worked since initial set up (coupling between gas valve and engine was also incorrectly installed sucking air) had to correct that at activation ( both units 10KK) my unit 11KW first outage she cut out 1300 code then display disappeared had new control board installed (I have ran it for 2 hours under load seems fine) is anyone else having this issue don’t know if it’s a vendor change or what
Quote
grsthegreat
Has anyone put a oil pressure guage on it to check pressures?
Quote
Peddler
Are they all the same models?  Are the SNs close together?
Quote
Ktdalka
Yes being told the unit that was installed about 6 weeks ago has pressure (hang on just contacted the motor is being replaced) and yes same vintage both 10KW both require motor changes
Quote
ohmslaw
Unit needs software update
Quote
Ktdalka
ohmslaw wrote:
Unit needs software update


generac sent it three times changing motor second unit approximately same vintage
Quote
ohmslaw
cant find bulletin the new 10 kw single cylinder units have a software issue.
the new firmware holds of fault longer.
Quote