Model #: 0865
Propane
Length of gas pipe feeding the generator: 8 ft
Size of gas pipe feeding the generator:3/4
How long since the last full maintenance: This year
How long have you experienced this problem: 2 days

Description of problem: The generator will switch over and start even when there is grid power available. It does this randomly, Thanks for looking
Niko
Quote
Skip Douglas SkipD
It sounds like you may have a poor connection on the N1/N2 lines between the transfer switch and the generator. Those lines having 240VAC between them is what keeps the generator satisfied that utility power exists.

The poor connection could be in the transfer switch (don't overlook the fuses that are in line with the connections), in the generator, or between the two.
Skip Douglas
Quote
gearheadniko
Thanks for the super quick response Skip, I have checked all the connections and all seems good. The generator has not started since I checked the connections. If it happens again I will shut down the power and redo all the "N" connectors. Thanks again for your help.
Niko
Quote
Canada_Guy
Does that model have a display on the generator control panel? If so, what does the history show?