  • RTSW200A3 used with older 2005 15KW

    Will the RTSW200A3 transfer switch work with the older 15KW (2005) generator? I see that all the newer generators have 5 control wires whereas my generator only uses 4. Is this a problem or will it work with just the 4?

  • #2
    Originally posted by jallis View Post
    Will the RTSW200A3 transfer switch work with the older 15KW (2005) generator? I see that all the newer generators have 5 control wires whereas my generator only uses 4. Is this a problem or will it work with just the 4?
    The wire not used should be the T1 wire, needed only by newer generators to power the built-in battery charger.

    Comment


    • #3
      Thankyou